Dimmer 40A, new dimmer 16/24A with big heating sink. Why is N wire thin?
to small for power 16/24/40A
Welcome!
Tap into the collective knowledge of our community by asking your questions in our forums, where helpful members are ready to assist you.
La domanda è stata contrassegnata
1
Rispondi
216
Visualizzazioni
Hi Olivier
The neutral wire connected to the zero-cross detector carries very little current (typically 5 – 10 mA). It does not power the load, so it can be much thinner.
More details in documentation: http://www.rbdimmer.com/knowledge/article/49#Hardware Connection
Thank you.