Dimmer 40A, wire N. Why is N wire thin?
Esta pregunta ha sido marcada
1
Responder
2233
Vistas
Hi Olivier
The neutral wire connected to the zero-cross detector carries very little current (typically 5 – 10 mA). It does not power the load, so it can be much thinner.
More details in documentation: http://www.rbdimmer.com/knowledge/article/49#Hardware Connection
Thank you.