Dimmer 40A, new dimmer 16/24A with big heating sink. Why is N wire thin?
to small for power 16/24/40A

Avatar
Discard

Hi  Olivier
The neutral wire connected to the zero-cross detector carries very little current (typically 5 – 10 mA). It does not power the load, so it can be much thinner.
More details in documentation:  http://www.rbdimmer.com/knowledge/article/49#Hardware Connection



Avatar
Discard
Author

Thank you.

Your Answer

Please try to give a substantial answer. If you wanted to comment on the question or answer, just use the commenting tool. Please remember that you can always revise your answers - no need to answer the same question twice. Also, please don't forget to vote - it really helps to select the best questions and answers!